Those of you with portable generators mounted on their travel trailers. Do you ground them? Do you have a ground wire attached to the trailer frame? Do you dangle a wire to ground when in use? Do you ignore it?

Attaching ground to the trailer frame seems to make the most sense, but is the trailer actually grounded? I mean, it’s sitting on rubber wheels. The stabilizers are sitting on plastic pads. The jack is sitting on either plastic pad or pieces of wood. Seems pretty isolated from ground as a whole to me.

Thoughts?
__________________

PamW is offline   Reply With Quote
Old 05-02-2017, 02:28 PM   #2
Senior Member
 
chily3's Avatar
 
Join Date: Jun 2014
Location: Sacramento
Posts: 573
California
We just use the three wire cord. No other grounding
__________________

__________________

Mike & Emily-Sacramento, CA
Our 4th trailer (2016 Aspen Trail 1900RB)
2018 F150 STX 2.7 Eco Boost
chily3 is offline   Reply With Quote
Old 05-02-2017, 06:47 PM   #3
Site Team
 
wahoonc's Avatar
 
Join Date: Jun 2014
Location: Sprung Leak
Posts: 3,157
North Carolina
Most portable generators don't require grounding under most applications. For the RV I wouldn't worry about it too much. When I had my Airstream with the dual Honda setup we didn't bother to ground anything, just plugged it and used it.

Aaron
__________________
There is madness to my methods
2015 Coleman CM16FBS(traded) 2016 Concord 300DS
2015 Ford Fusion Hybrid following along
wahoonc is offline   Reply With Quote
Old 05-03-2017, 12:00 AM   #4
Senior Member
 
Join Date: Jul 2014
Location: Dalzell
Posts: 714
South Carolina
There is a point to be made here. The chassis ground of a generator is not normally tied to the neutral side of the voltage output, like it is in a house or camper pedestal outlet. There are lots of stories why this is so, but the end result is that when you plug your shore power plug into a generator outlet, the chassis ground is not connected to the return (white wire) in an AC outlet. That can cause problems for voltage and circuit monitors, like surge protectors. To overcome this, it is common to wire the ground (green) to the neutral (white) in a regular 120 volt, 15 amp, 3-prong plug, and plug it into the generator's 110Volt outlet. That will tie the two together and alleviate these malfunctions. Just a simple plug, with a 1" jumper inside, marked as "Grd to Neu connector" or words to that effect.
MartyG is offline   Reply With Quote
Old 05-03-2017, 01:28 AM   #5
Senior Member
 
Join Date: Dec 2016
Location: Delaware
Posts: 227
Ohio
Thank you folks. I play electrical engineer during the day and tend to overthink things occasionally. I also make clear to anyone who listens that I play engineer, not electrician. I know theory (mostly), not real life installation! I assumed no ground was necessary, until the instructions suggested otherwise.

Found this, which makes me more comfortable.

2014 NEC

250.34(A) Portable Generators.
The frame of a portable generator shall not be required to be connected to a grounding electrode as defined in 250.52 for a system supplied by the generator under the following conditions:

1. The generator supplies only equipment mounted on the generator, cord-and-plug-connected equipment through receptacles mounted on the generator, or both, and

2. The normally non-current-carrying metal parts of equipment and the equipment grounding conductor terminals of the receptacle are connected to the generator frame.

Marty, thank you for your input I'll know what's wrong if my gfci at my sink keeps tripping after forgetting the trick with the plug!


Sent from my SM-N910V using Tapatalk
__________________
2017 CTS16FB
2019 Nissan NV
PamW is offline   Reply With Quote
Old 05-03-2017, 01:32 AM   #6
Site Team
 
wahoonc's Avatar
 
Join Date: Jun 2014
Location: Sprung Leak
Posts: 3,157
North Carolina
Check out the specific generator, some are bonded neutral, others are floating neutral. The bonded ones will play fine with a GFCI.

Aaron[emoji41]

Sent from my XT1254 using Tapatalk
__________________
There is madness to my methods
2015 Coleman CM16FBS(traded) 2016 Concord 300DS
2015 Ford Fusion Hybrid following along
wahoonc is offline   Reply With Quote
Old 05-03-2017, 01:34 AM   #7
Senior Member
 
Join Date: Dec 2016
Location: Delaware
Posts: 227
Ohio
Quote:
Originally Posted by wahoonc View Post
Check out the specific generator, some are bonded neutral, others are floating neutral. The bonded ones will play fine with a GFCI.

Aaron[emoji41]

Sent from my XT1254 using Tapatalk
Mine is a cheap no name brand. I'll assume the worst! [emoji6] But I probably won't do anything about it until I see problems because, well, memory. [emoji23]

Sent from my SM-N910V using Tapatalk
__________________
2017 CTS16FB
2019 Nissan NV
PamW is offline   Reply With Quote
Old 05-03-2017, 01:35 AM   #8
Site Team
 
wahoonc's Avatar
 
Join Date: Jun 2014
Location: Sprung Leak
Posts: 3,157
North Carolina
Quote:
Originally Posted by PamW View Post
Mine is a cheap no name brand. I'll assume the worst! [emoji6] But I probably won't do anything about it until I see problems because, well, memory. [emoji23]

Sent from my SM-N910V using Tapatalk
Define "cheap no name brand"...

Aaron[emoji41]

Sent from my XT1254 using Tapatalk
__________________
There is madness to my methods
2015 Coleman CM16FBS(traded) 2016 Concord 300DS
2015 Ford Fusion Hybrid following along
wahoonc is offline   Reply With Quote
Old 05-03-2017, 01:38 AM   #9
Senior Member
 
Join Date: Dec 2016
Location: Delaware
Posts: 227
Ohio
Wen 2000w

Inverter style, bought from Woot.com for $330.

At least no-name to me at the time.

Sent from my SM-N910V using Tapatalk
__________________
2017 CTS16FB
2019 Nissan NV
PamW is offline   Reply With Quote
Old 05-03-2017, 01:43 AM   #10
Senior Member
 
Join Date: Dec 2016
Location: Delaware
Posts: 227
Ohio
Quote:
Originally Posted by PamW View Post
Wen 2000w

Inverter style, bought from Woot.com for $330.

At least no-name to me at the time.

Sent from my SM-N910V using Tapatalk
http://www.wenproducts.com/store/gen...nerator-56200i


Sent from my SM-N910V using Tapatalk
__________________
2017 CTS16FB
2019 Nissan NV
PamW is offline   Reply With Quote
Old 05-03-2017, 01:46 AM   #11
Site Team
 
wahoonc's Avatar
 
Join Date: Jun 2014
Location: Sprung Leak
Posts: 3,157
North Carolina
Quote:
Originally Posted by PamW View Post
Wen 2000w

Inverter style, bought from Woot.com for $330.

At least no-name to me at the time.

Sent from my SM-N910V using Tapatalk
I will check it out tomorrow. I have heard of it, but I am not familiar with them.

BTW... I am a lot of design engineers worst nightmares... I am the guy in the field that installs it AND makes it work! [emoji3]

Aaron[emoji41]

Sent from my XT1254 using Tapatalk
__________________
There is madness to my methods
2015 Coleman CM16FBS(traded) 2016 Concord 300DS
2015 Ford Fusion Hybrid following along
wahoonc is offline   Reply With Quote
Old 05-03-2017, 01:54 AM   #12
Senior Member
 
Join Date: Dec 2016
Location: Delaware
Posts: 227
Ohio
Quote:
Originally Posted by wahoonc View Post
I will check it out tomorrow. I have heard of it, but I am not familiar with them.

BTW... I am a lot of design engineers worst nightmares... I am the guy in the field that installs it AND makes it work! [emoji3]

Aaron[emoji41]

Sent from my XT1254 using Tapatalk
When I used to do a lot of construction administration the first thing I would say upon meeting a contractor for the first time was, "just because it makes sense to me in black and white on paper doesn't mean it necessarily makes sense in real life"! (but that doesn't mean I was a pushover either!)

I just noticed a wiring diagram in the user manual, let's see how good and confused I can make myself! (and I wonder how accurate it is, or if it's made like our Colemans! [emoji6])

Sent from my SM-N910V using Tapatalk
__________________
2017 CTS16FB
2019 Nissan NV
PamW is offline   Reply With Quote
Old 05-03-2017, 02:03 AM   #13
Senior Member
 
Join Date: Dec 2016
Location: Delaware
Posts: 227
Ohio
Quote:
Originally Posted by wahoonc View Post
I will check it out tomorrow. I have heard of it, but I am not familiar with them.

BTW... I am a lot of design engineers worst nightmares... I am the guy in the field that installs it AND makes it work! [emoji3]

Aaron[emoji41]

Sent from my XT1254 using Tapatalk
If I'm reading it right... On the plug it's showing hot to hot, neutral to neutral and ground to ground to the ground screw on the front of the unit.

I suppose I could send them an email and ask...what a concept!

Sent from my SM-N910V using Tapatalk
__________________
2017 CTS16FB
2019 Nissan NV
PamW is offline   Reply With Quote
Old 05-03-2017, 02:08 AM   #14
Senior Member
 
Join Date: Jul 2014
Location: Dalzell
Posts: 714
South Carolina
I found the article which taught me about Ground-Neutral Bonding. As you read the comments at the end, there is an on-going discussion as to why, but most agree to do it.
As to Wen, I had one of their soldering guns way back in the 60's. They've been around a long time, have a respectable web site and line of electrical tools.

Here's the grounding link: Generator Ground-Neutral Bonding | No~Shock~Zone
MartyG is offline   Reply With Quote
Old 05-03-2017, 04:47 PM   #15
Senior Member
 
Firstime RVer's Avatar
 
Join Date: Jan 2016
Location: allentown
Posts: 246
New Jersey
Not sure if I can make this simple..


Grounding connections are to take any stray current caused by bare wires or dripping water etc. and run it safely to ground along the path of least resistance. This keeps you and me from being the path of least resistance to ground.


If you picture your generator as a battery. You can touch the positive or negative terminals of the battery without getting shocked.. Touch both terminals at the same time and it would be a shocking experience..


Now if you connected the negative terminal to a rod in the ground (called an earth ground) and touched the positive terminal with one hand, and the ground with the other, you will get zapped because you are the path of least resistance to ground.. The ground connections inside your rv protect you inside the trailer. So connecting the generator ground to earth ground doesn't really buy you anything inside or outside the trailer..


On shore power since the neutral is connected to earth ground thru your power cord, there is now a risk outside your rv. That's why GFCI's are used..


hope this makes sense
__________________
Pat & Barb
2019 5.3L ECOTEC3 V8 Chevy Silverado 1500
2016 Aspen Trail 1900RB
Allentown, NJ
Firstime RVer is offline   Reply With Quote
Old 05-03-2017, 07:04 PM   #16
Senior Member
 
Join Date: Jul 2014
Location: Dalzell
Posts: 714
South Carolina
I was with you until the last two sentences:
Quote:
Originally Posted by Firstime RVer View Post
....The ground connections inside your rv protect you inside the trailer. So connecting the generator ground to earth ground doesn't really buy you anything inside or outside the trailer..
On shore power since the neutral is connected to earth ground thru your power cord, there is now a risk outside your rv. That's why GFCI's are used..
hope this makes sense
The TT is only designed for shore power, unless it has a built-in generator. Using a portable generator is not within their design. As such, the chassis of the trailer is indeed tied to the chassis of the generator, through the ground prong of the connector. However, none of it is directly grounded. Thus, stray voltage can find a path somehow to ground, and it's dangerous if that path is through a human body. That's why (although nobody pays attention) that every portable generator owner's manual says to ground the generator chassis to an earth ground.
There are other reasons, previously noted, for tying neutral to ground. But you're off a little on the purpose of a GFCI. They work by measuring the current coming in from the hot side, and flowing out the neutral side. They should be the same. If the two vary by just a few milliamps, the voltage must be going somewhere else, rather than the desired path. It could be a leak to chassis ground, but more dangerously, through a human to get to that ground. The GFCI trips when the "in" and "out" don't match, within some given tolerance.
Finally, I agree that when you are plugged into a properly-wired outlet, that the pedestal, or house wiring effectively bonds the neutral to the ground, and extends that ground to the TT chassis. But I do not understand your statement, "...there is now a risk outside your rv. "
MartyG is offline   Reply With Quote
Old 05-03-2017, 08:17 PM   #17
Senior Member
 
Firstime RVer's Avatar
 
Join Date: Jan 2016
Location: allentown
Posts: 246
New Jersey
Hi Marty,
I don't think we are disagreeing.. I was trying to make the point that since a generator that is not grounded to earth has a floating ground that stray currents between the generator power and earth ground don't represent much of a risk.
On shore power the risk of stray currents to earth ground are much higher..
In both cases GFCI's are lifesavers...
All the best.
Pat


Ps I prefer, not being able to reset a GFCI as an indication of a problem, to the "tingles" we used to get in the old days when something was wrong...
__________________
Pat & Barb
2019 5.3L ECOTEC3 V8 Chevy Silverado 1500
2016 Aspen Trail 1900RB
Allentown, NJ
Firstime RVer is offline   Reply With Quote
Old 05-03-2017, 08:37 PM   #18
Senior Member
 
Join Date: Jul 2014
Location: Dalzell
Posts: 714
South Carolina
Pat, you are correct; we are not disagreeing. I hear you more clearly now. You're saying that a generator, not grounded to earth, (and I guess) especially when the neutral is not tied to chassis ground) then a hazardous path to ground is less of a threat. Interesting point of view. Will welcome the opinions of others on that. We agree on the benefits of GFCIs, and yes, I remember the "tingles!" Best to you, too!
MartyG is offline   Reply With Quote
Old 05-03-2017, 09:45 PM   #19
Senior Member
 
Firstime RVer's Avatar
 
Join Date: Jan 2016
Location: allentown
Posts: 246
New Jersey
I'm no expert, which becomes more obvious to me with each passing day..
So I'd also like to get other opinions as well..
__________________
Pat & Barb
2019 5.3L ECOTEC3 V8 Chevy Silverado 1500
2016 Aspen Trail 1900RB
Allentown, NJ
Firstime RVer is offline   Reply With Quote
Old 05-04-2017, 01:02 AM   #20
Site Team
 
wahoonc's Avatar
 
Join Date: Jun 2014
Location: Sprung Leak
Posts: 3,157
North Carolina
Even the 'experts' can't agree. My company dictates that ALL generators in use on a job site WILL be grounded. Some manuals say you have to, some manuals say per the local codes, same don't say at all. I have worked on sites all over the country, some want generators grounded some will tell you not to. Just for the record we have everything from 1500 watt Honda inverters all the way up to a couple of 17kw 3 phase diesel monsters.

On a personal level I think grounding is a probably a good idea, however a true grounding rod according to the NEC has to be driven in the ground and has to be at least 8' long... NEC 250.52(A)(5) states: “Rods and pipe electrodes
shall not be less than 2.44 m (8 ft.) in length.”
Now how many of you are lugging around an 8' grounding rod and a means to drive it 7'+ into the ground.

When working on buildings we can usually get our hands on a good ground via the steel frame, the lightning protection system of even the building electrical ground. Cold water pipes used to be a good ground, not so much anymore since they have switch to plastic plumbing.

Aaron
__________________

__________________
There is madness to my methods
2015 Coleman CM16FBS(traded) 2016 Concord 300DS
2015 Ford Fusion Hybrid following along
wahoonc is offline   Reply With Quote
Reply


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


» Featured Campgrounds

Reviews provided by

Disclaimer:

This website is not affiliated with or endorsed by Dutchmen RV or any of its affiliates. This is an independent, unofficial site.


All times are GMT. The time now is 07:04 PM.


Powered by vBulletin® Version 3.8.7
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Copyright 2020 Social Knowledge, LLC All Rights Reserved.
×