Quote:
Originally Posted by wahoonc View Post
I will have to dig up the picture of the 20 amp plug that I found on one of my jobsites...

20 amp plug has the sideways blade, guys didn't have any heavy duty cords (aren't supposed to run this particular 20 amp equipment on a drop cord, but that is a different story) so the grabbed the sideways blade twisted it 90 degrees and plugged it into a 15 amp drop cord, melted the plug pretty good trying to haul too many amps across it. I found it, cut it off and left them with out the piece of equipment for a couple of days as a lesson. Plug went into my training box of things not to do.

Every time you make something idiot proof a different idiot comes along and defeats it.

Aaron
Ordinarily, a 20 amp socket has both the sideways and the "normal"... If they had a 20 amp drill attempting to use it on a 15 amp circuit, i get it... I would have done the same thing instead of standing around waiting for something to happen.
__________________

franktafl is offline   Reply With Quote
Old 02-25-2019, 11:40 PM   #22
Senior Member
 
Join Date: Jun 2016
Location: Capron
Posts: 413
Illinois
I have wired houses, installed sub panels, AC, HVAC, generator transfer switches, etc. But still for the life of me cannot grasp the concept of three phase! LOL
__________________

acdii is offline   Reply With Quote
Old 02-26-2019, 11:12 AM   #23
Senior Member
 
Join Date: Jun 2017
Location: Wesley Chapel
Posts: 3,066
Florida
Quote:
Originally Posted by acdii View Post
I have wired houses, installed sub panels, AC, HVAC, generator transfer switches, etc. But still for the life of me cannot grasp the concept of three phase! LOL

LOL... Simple if you are trained in it.
franktafl is offline   Reply With Quote
Old 02-26-2019, 02:30 PM   #24
Senior Member
 
Join Date: Jun 2016
Location: Capron
Posts: 413
Illinois
Quote:
Originally Posted by franktafl View Post
LOL... Simple if you are trained in it.



I've wired it, used to work in a factory as maintenance, but the concept of how it works eludes me. Then again, that was 35 years ago! LOL I haven't touched 3 Phase since.
acdii is offline   Reply With Quote
Old 02-26-2019, 02:51 PM   #25
Senior Member
 
Join Date: Jun 2017
Location: Wesley Chapel
Posts: 3,066
Florida
Quote:
Originally Posted by acdii View Post
I've wired it, used to work in a factory as maintenance, but the concept of how it works eludes me. Then again, that was 35 years ago! LOL I haven't touched 3 Phase since.
hasn't changed at all...
franktafl is offline   Reply With Quote
Old 02-26-2019, 02:57 PM   #26
Senior Member
 
Join Date: Jun 2016
Location: Capron
Posts: 413
Illinois
Quote:
Originally Posted by franktafl View Post
hasn't changed at all...

No, but I have!
acdii is offline   Reply With Quote
Old 02-26-2019, 03:01 PM   #27
Senior Member
 
Join Date: Jun 2017
Location: Wesley Chapel
Posts: 3,066
Florida
Quote:
Originally Posted by acdii View Post
No, but I have!
LOL! For the better I hope...
franktafl is offline   Reply With Quote
Old 02-26-2019, 09:41 PM   #28
Senior Member
 
Join Date: Jan 2018
Location: Beaver Dam
Posts: 895
Wisconsin
Quote:
Originally Posted by franktafl View Post
That's ok, you understand it enough to be able to identify it. I'm sure PERSISTANT will be along to give a complete and very detailed explanation.
Thanks for the vote of confidence Frank. Wasn't it you who straitened be out on this a few months ago?
__________________
Paul Bristol
Dutchman Kodiak Cub KD176RD 2018
Nissan Pathfinder 2015
persistent is offline   Reply With Quote
Old 02-26-2019, 09:56 PM   #29
Senior Member
 
Join Date: Jun 2017
Location: Wesley Chapel
Posts: 3,066
Florida
Quote:
Originally Posted by persistent View Post
Thanks for the vote of confidence Frank. Wasn't it you who straitened be out on this a few months ago?
have you been drinking already?
franktafl is offline   Reply With Quote
Old 03-03-2019, 01:43 AM   #30
Senior Member
 
Join Date: Jan 2019
Location: Grand Junction
Posts: 89
Colorado
110v ??

All my house sockets measure about 120V. Haven't seen 110V in years, unless the circuit was overloaded. Strange how everyone still calls it 110V...
leisuresolar@gmail.com is offline   Reply With Quote
Old 03-03-2019, 11:31 AM   #31
Site Team
 
wahoonc's Avatar
 
Join Date: Jun 2014
Location: Sprung Leak
Posts: 3,157
North Carolina
Quote:
Originally Posted by leisuresolar@gmail.com View Post
All my house sockets measure about 120V. Haven't seen 110V in years, unless the circuit was overloaded. Strange how everyone still calls it 110V...
I was curious so did a bit of digging; 110 volt was the original set up by Edison, it delivered 100 volts nominal, by the 1930's it had increased to 115 volts, but was not codified until 1968. Around 1984 ANSI/NEC set the standard for residential to 120 volts +/- 5%. And that is where we are today.

Aaron
__________________
There is madness to my methods
2015 Coleman CM16FBS(traded) 2016 Concord 300DS
2015 Ford Fusion Hybrid following along
wahoonc is offline   Reply With Quote
Old 03-03-2019, 02:55 PM   #32
Senior Member
 
ArmyVeteran's Avatar
 
Join Date: Oct 2017
Location: Aiken
Posts: 702
South Carolina
We are just old. And not necessarily any wiser either :-)
ArmyVeteran is offline   Reply With Quote
Old 03-03-2019, 03:04 PM   #33
Senior Member
 
Join Date: Jun 2016
Location: Capron
Posts: 413
Illinois
Right and same with 220, it is actually 240v. So if you say 120/220, then it is incorrect, if you say 110/220, it matches but is still incorrect, so in actuality it is 120/240v. To get 240 it doubles the poles, and is fed off two separate busses from the main panel.



Going way way back to when I studied electronics for a career that thankfully never happened, TV and VCR repair, I recall something about how 120v came about from the frequency of the generation, 60hz. Since AC runs positive to negative to the neutral, doubling it gave 120. But then again that was like nearly 40 years ago, and I have not studied any of that since.
acdii is offline   Reply With Quote
Old 03-03-2019, 03:12 PM   #34
Senior Member
 
Join Date: Jun 2017
Location: Wesley Chapel
Posts: 3,066
Florida
Quote:
Originally Posted by ArmyVeteran View Post
We are just old. And not necessarily any wiser either :-)
have you hit the ceiling on wise? it's good to be old but better to be older!
franktafl is offline   Reply With Quote
Old 03-03-2019, 03:20 PM   #35
Senior Member
 
Join Date: Jun 2017
Location: Wesley Chapel
Posts: 3,066
Florida
Quote:
Originally Posted by acdii View Post
Right and same with 220, it is actually 240v. So if you say 120/220, then it is incorrect, if you say 110/220, it matches but is still incorrect, so in actuality it is 120/240v. To get 240 it doubles the poles, and is fed off two separate busses from the main panel.



Going way way back to when I studied electronics for a career that thankfully never happened, TV and VCR repair, I recall something about how 120v came about from the frequency of the generation, 60hz. Since AC runs positive to negative to the neutral, doubling it gave 120. But then again that was like nearly 40 years ago, and I have not studied any of that since.
Strictly speaking, the voltages we have been talking about have belonged to the US and mostly North America. The rest of the world relies on 50Hz rather than 60 and the voltages are greater per outlet than the US. here's a map to 'splain

https://en.wikipedia.org/wiki/Electr...,_Detailed.svg

being in the electrical bizness, makes me learn this sort of stuff and being an RCDD incorporates low voltages internationally.
franktafl is offline   Reply With Quote
Old 03-03-2019, 04:13 PM   #36
Senior Member
 
Join Date: Jun 2016
Location: Capron
Posts: 413
Illinois
Well if I ever turn my RV into a Caravan, I will make sure to up it to 230v for the European standards! Japan is 50hz and 100 volts in some areas, so guess I wont be taking it there anytime soon.
acdii is offline   Reply With Quote
Old 03-03-2019, 08:22 PM   #37
Senior Member
 
Join Date: Jan 2018
Location: Beaver Dam
Posts: 895
Wisconsin
120 volts is the maximum standard. 110 volts is the minimum standard. 115 is the nominal voltage.
My household voltage is usually 118 to 120 volts.


oops, someone else already answered this.
__________________
Paul Bristol
Dutchman Kodiak Cub KD176RD 2018
Nissan Pathfinder 2015
persistent is offline   Reply With Quote
Old 03-05-2019, 09:35 AM   #38
Site Team
 
wahoonc's Avatar
 
Join Date: Jun 2014
Location: Sprung Leak
Posts: 3,157
North Carolina
Quote:
Originally Posted by persistent View Post
120 volts is the maximum standard. 110 volts is the minimum standard. 115 is the nominal voltage.
My household voltage is usually 118 to 120 volts.


oops, someone else already answered this.
Need to move

Ours sits around 124 volts and we are at the end of the line. I seldom see anything below 120 volts even during peak season with all the A/Cs running.

We are on a EMC (co-op) and have outstanding service, even when a string of tornadoes wiped out several transformer yards we had power back within less than 48 hours.

Aaron
__________________
There is madness to my methods
2015 Coleman CM16FBS(traded) 2016 Concord 300DS
2015 Ford Fusion Hybrid following along
wahoonc is offline   Reply With Quote
Old 03-05-2019, 02:21 PM   #39
Senior Member
 
sundancer 87's Avatar
 
Join Date: Dec 2012
Location: Tahlequah
Posts: 3,079
Oklahoma
Quote:
Originally Posted by acdii View Post
Well if I ever turn my RV into a Caravan, I will make sure to up it to 230v for the European standards! Japan is 50hz and 100 volts in some areas, so guess I wont be taking it there anytime soon.

Want a head scratcher? Try southern hemisphere 240, two wire electricity. One leg, load and return and the color code can be blue and brown or black and red. Sometimes a ground or earth and in the older load centers or switchboards replaceable wire fuses. Circuits breakers are being used now but the busses are different.
Wire sizes are set in actual wire size and not AWG sizes.
__________________
2013 Voltage 3800, 2012 Chevy 3500 HD
2010 Yamaha V Star 950
2009 Yamaha Raider
Volunteering with Habitat for Humanity Caravanners
sundancer 87 is offline   Reply With Quote
Old 03-19-2019, 10:26 PM   #40
Senior Member
 
ArmyVeteran's Avatar
 
Join Date: Oct 2017
Location: Aiken
Posts: 702
South Carolina
Quote:
Originally Posted by franktafl View Post
have you hit the ceiling on wise? it's good to be old but better to be older!



I have slept since I made that remark.



Interesting enough, the older I got the wiser my Father was.......hmmm
__________________

ArmyVeteran is offline   Reply With Quote
Reply


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


» Featured Campgrounds

Reviews provided by

Disclaimer:

This website is not affiliated with or endorsed by Dutchmen RV or any of its affiliates. This is an independent, unofficial site.


All times are GMT. The time now is 08:54 AM.


Powered by vBulletin® Version 3.8.7
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Copyright 2020 Social Knowledge, LLC All Rights Reserved.
×