2015 3990 Living Room A/C
Anyone out there with a 2015 3990 with three A/C's? I'm thinking that they didn't finish venting my living room A/C. I only have the puck vents in the living room as well as two larger house type metal vents in the ceiling. No actual unit suspended from the ceiling like in the garage or bedroom. I want to change the filters but can't find them. Is yours similar? Thanks.
Rusty
__________________
__________________
2015 Black F-350 Platinum Diesel Dually Crew Cab
2019 Riverstone Legacy 38MB (Full Paint/All Options)
2015 Voltage 3990 (Full Paint, All Options) Sold 6/18
2005 Harley Ultra Classic w/too many miles
|
|
|
08-11-2015, 01:35 PM
|
#2
|
Senior Member
Join Date: Dec 2012
Location: Tahlequah
Posts: 3,079
Oklahoma
|
The metal vents are the return air vents. The foam filters are in there. The A/C proper is on the roof and is ducted to the four discharge openings.
You will want to search A/C problems to learn how to remove the A/C on the roof and properly seal the duct work up there to maximize cold air flow. You will be amazed what you find there.
__________________
__________________
2013 Voltage 3800, 2012 Chevy 3500 HD
2010 Yamaha V Star 950
2009 Yamaha Raider
Volunteering with Habitat for Humanity Caravanners
|
|
|
08-11-2015, 10:54 PM
|
#3
|
Senior Member
Join Date: Jan 2015
Location: Roselle
Posts: 1,292
Illinois
|
Thanks for the response. On my way home from Sturgis/Colorado. First task on my list.
Rusty
__________________
2015 Black F-350 Platinum Diesel Dually Crew Cab
2019 Riverstone Legacy 38MB (Full Paint/All Options)
2015 Voltage 3990 (Full Paint, All Options) Sold 6/18
2005 Harley Ultra Classic w/too many miles
|
|
|
08-11-2015, 11:56 PM
|
#4
|
Senior Member
Join Date: Nov 2013
Location: Quartzsite
Posts: 682
Arizona
|
[QUOTE=sundancer 87;30392]The metal vents are the return air vents. The foam filters are in there. The A/C proper is on the roof and is ducted to the four discharge openings./QUOTE]
In my 3905 I have nine discharge openings. Four in living room, two in garage, two in bedroom, and one in bathroom.
I also find that my garage A/C is ducted forward into the same system though the flow doesn't get must past the two garage ceiling ducts.
__________________
2013 Voltage 3905
2013 F350 4x4 DRW
2013 RZR XP 900
|
|
|
08-12-2015, 12:31 AM
|
#5
|
Senior Member
Join Date: Dec 2012
Location: Tahlequah
Posts: 3,079
Oklahoma
|
[QUOTE=arlan in arizona;30445]
Quote:
Originally Posted by sundancer 87
The metal vents are the return air vents. The foam filters are in there. The A/C proper is on the roof and is ducted to the four discharge openings./QUOTE]
In my 3905 I have nine discharge openings. Four in living room, two in garage, two in bedroom, and one in bathroom.
I also find that my garage A/C is ducted forward into the same system though the flow doesn't get must past the two garage ceiling ducts.
|
Yep, I have nine discharge vents also but my comment regarding four vents were in direct response to the OP's question containing the words 'living room'.
__________________
2013 Voltage 3800, 2012 Chevy 3500 HD
2010 Yamaha V Star 950
2009 Yamaha Raider
Volunteering with Habitat for Humanity Caravanners
|
|
|
08-12-2015, 12:57 AM
|
#6
|
Senior Member
Join Date: Sep 2014
Location: Callaway
Posts: 864
Maryland
|
[QUOTE=arlan in arizona;30445]
Quote:
Originally Posted by sundancer 87
The metal vents are the return air vents. The foam filters are in there. The A/C proper is on the roof and is ducted to the four discharge openings./QUOTE]
In my 3905 I have nine discharge openings. Four in living room, two in garage, two in bedroom, and one in bathroom.
I also find that my garage A/C is ducted forward into the same system though the flow doesn't get must past the two garage ceiling ducts.
|
Your bedroom and garage units are ducted? What type of ceiling plenum do you have in the garage?
Thanks
Cale
__________________
TV: 2015 F-350 DRW, CC, 4x4, with 14k GVWR package, 98 gallon TransferFlow Aux Tank, Timbren Shocks
TH: 2014 Voltage 3950, Sailun S637 all around
|
|
|
08-12-2015, 01:03 AM
|
#7
|
New Member
Join Date: Jul 2015
Posts: 7
|
2015 3990 Living Room A/C
Quote:
Originally Posted by lcv800
Thanks for the response. On my way home from Sturgis/Colorado. First task on my list.
Rusty
|
Rusty,
I'm in this same boat as you with the living room AC on my 3818 and I to just got back from Sturgis and Colorado.
Luke
|
|
|
08-12-2015, 01:10 AM
|
#8
|
Senior Member
Join Date: Nov 2013
Location: Quartzsite
Posts: 682
Arizona
|
[QUOTE=calewjohnson;30448]
Quote:
Originally Posted by arlan in arizona
Your bedroom and garage units are ducted? What type of ceiling plenum do you have in the garage?
Thanks
Cale
|
Only the garage unit is tied into the duct system. The bedroom in not. The plenum in the bedroom has vents that blow fore and aft. The garage unit plenum kind of sucks. It blows out the bottom but only seems to move air toward the driver side of the trailer and into the ceiling ducts. The movement to the duct system is slight, but it is there.
If your is like mine. Turn on ONLY the garage A/C and see if you feel air movement at the two ceiling ducts in the garage. I can also feel a slight amount or air movement at the two rear ceiling ducts in the living room but that's about as far as it can be felt.
Arlan
__________________
2013 Voltage 3905
2013 F350 4x4 DRW
2013 RZR XP 900
|
|
|
08-12-2015, 01:47 AM
|
#9
|
Senior Member
Join Date: Dec 2012
Location: Tahlequah
Posts: 3,079
Oklahoma
|
[QUOTE=calewjohnson;30448]
Quote:
Originally Posted by arlan in arizona
Your bedroom and garage units are ducted? What type of ceiling plenum do you have in the garage?
Thanks
Cale
|
Yep, two ducted pucks in the bed room and two in the garage.
The bed room has its own A/C that has a modified down discharge vent. However, a small movement of cold air from the living room A/C comes out of the down discharge vent.
I can't figure out where it is getting the air since I have pretty much taped closed the two ducts in there.
__________________
2013 Voltage 3800, 2012 Chevy 3500 HD
2010 Yamaha V Star 950
2009 Yamaha Raider
Volunteering with Habitat for Humanity Caravanners
|
|
|
08-12-2015, 03:23 AM
|
#10
|
Senior Member
Join Date: Sep 2014
Location: Callaway
Posts: 864
Maryland
|
Arlan and Sundancer...
Interesting...my garage is stand alone, while my bedroom is tied in, which I find to be better maybe?!?!
I keep the rear pucks closed and only let the rear AC do the garage. I leave the bedroom plenum closed, and let the bedroom cool via the two pucks...when the front is running, the main is invariably running, I get more air through the ducts to help with the living area.
I have had the puck lights down before near my loft, there is a lot of air that escapes through there when the AC is running, obviously something was left unsealed. I think the only way to fix that would be to tackle it if/when a new roof gets put on. The ceiling lights could be a source of air into your garage??
Cale
|
|
|
08-12-2015, 04:05 AM
|
#11
|
Senior Member
Join Date: Nov 2013
Location: Quartzsite
Posts: 682
Arizona
|
I'm glad this discussion came up. I would love to be able to put my garage air-conditioner in my bedroom and vice versa. I guess I will have to take a look at that when it cools off out here in a couple months.
__________________
2013 Voltage 3905
2013 F350 4x4 DRW
2013 RZR XP 900
|
|
|
08-12-2015, 07:32 AM
|
#12
|
Senior Member
Join Date: Aug 2013
Location: Memphis
Posts: 1,616
Michigan
|
Quote:
Originally Posted by calewjohnson
Arlan and Sundancer...
Interesting...my garage is stand alone, while my bedroom is tied in, which I find to be better maybe?!?!
I keep the rear pucks closed and only let the rear AC do the garage. I leave the bedroom plenum closed, and let the bedroom cool via the two pucks...when the front is running, the main is invariably running, I get more air through the ducts to help with the living area.
I have had the puck lights down before near my loft, there is a lot of air that escapes through there when the AC is running, obviously something was left unsealed. I think the only way to fix that would be to tackle it if/when a new roof gets put on. The ceiling lights could be a source of air into your garage??
Cale
|
Cale - mine is the same as yours. Odd how different these things are being built day to day
__________________
2019 Ram 3500 Limited w/ Max Tow pkg
2005 Cardinal 33LX
2014-3950, Full Paint, 17.5" tires, 370W solar, 3100W Magnum inverter w/ AGS, 7500w diesel generator, Micro-Air Easy Start 364 (x3) SOLD!
|
|
|
08-12-2015, 09:57 AM
|
#13
|
Senior Member
Join Date: Sep 2014
Location: Callaway
Posts: 864
Maryland
|
Quote:
Originally Posted by donzinger
Cale - mine is the same as yours. Odd how different these things are being built day to day
|
No kidding, completely boggles my mind. They could be so much more efficient and quality of work may accidentally increase if they were to do things the same from trailer to trailer.....
|
|
|
08-12-2015, 10:52 AM
|
#14
|
Senior Member
Join Date: Aug 2013
Location: Memphis
Posts: 1,616
Michigan
|
I may actually look into finding a diffuser for the bedroom AC like the garage has - I finally climbed up there last night in my troubleshooting my LMS shedding issue and I like it - however I did find a loose piece of foam rubber in there sitting over the intake grille - it is supposed to be in there somewhere as it is nicely cut and has a label indicating which side is to face the front of the AC unit - anyone have any ideas? For now, I just pushed it out of the way and viola - plenty of airflow.
__________________
2019 Ram 3500 Limited w/ Max Tow pkg
2005 Cardinal 33LX
2014-3950, Full Paint, 17.5" tires, 370W solar, 3100W Magnum inverter w/ AGS, 7500w diesel generator, Micro-Air Easy Start 364 (x3) SOLD!
|
|
|
08-12-2015, 11:20 AM
|
#15
|
Senior Member
Join Date: Sep 2014
Location: Callaway
Posts: 864
Maryland
|
Quote:
Originally Posted by donzinger
I may actually look into finding a diffuser for the bedroom AC like the garage has - I finally climbed up there last night in my troubleshooting my LMS shedding issue and I like it - however I did find a loose piece of foam rubber in there sitting over the intake grille - it is supposed to be in there somewhere as it is nicely cut and has a label indicating which side is to face the front of the AC unit - anyone have any ideas? For now, I just pushed it out of the way and viola - plenty of airflow.
|
I don't think the plenum in the garage (for the 3950) will work in the bedroom. I think they are specific for vented and non vented applications....however, my next project is to come up with a way to use a regular home filter and have a close able vent, much like a home ceiling register installed in that spot.
Cale
|
|
|
08-17-2015, 08:18 PM
|
#16
|
Member
Join Date: Sep 2013
Location: Annandale
Posts: 35
Virginia
|
Quote:
Originally Posted by calewjohnson
Arlan and Sundancer...
Interesting...my garage is stand alone, while my bedroom is tied in, which I find to be better maybe?!?!
I keep the rear pucks closed and only let the rear AC do the garage. I leave the bedroom plenum closed, and let the bedroom cool via the two pucks...when the front is running, the main is invariably running, I get more air through the ducts to help with the living area.
I have had the puck lights down before near my loft, there is a lot of air that escapes through there when the AC is running, obviously something was left unsealed. I think the only way to fix that would be to tackle it if/when a new roof gets put on. The ceiling lights could be a source of air into your garage??
Cale
|
Same on my 3905!
__________________
__________________
2011 HD Chevrolet Crew Cab Dually w/Duramax
2014 Voltage 3905 Epic III, full body paint
1999 FLHR, Raptor 700R, TT-230, TT-125LE
|
|
|
|
Posting Rules
|
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts
HTML code is Off
|
|
|
|
» Recent Discussions |
|
|
|
|
|
|
|
|
|
|
|
|
|
|
|
|