Solar Panel Layout and Cabling for Coleman CTS192

Attached is a solar panel layout which might work for my TT. I designed it wanting to maximize winter solar with tilting South facing panels. A problem with this is the wire length between the panels and the MPPT controller on my <23’ TT (bumper to hitch). I want the panels in parallel so partial shading of one panel does not dramatically impact the power output of the whole bank, as in series connections. A combination of parallel and the cable run leads to a voltage drop incompatible with the MPPT controller according to Renogy.



If anyone has gotten around this voltage drop problem, maybe a really wide diameter cable, I'd like to hear the solution. Another problem is getting the cables to the MPPT controller in the battery box without duct taping the solar output cable to the face of the TT. I'm thinking I could run the cable through the refrigerator vent, through the floor, and then under the TT to the battery box but that seems unsafe - kind of like that rubber propane hose running under the TT



I’d also like to contact any recommended electricians or solar experts in the Frederick County VA area about this solar setup and some other TT 12Volt and AC wiring issues.


Thanks!
Attached Thumbnails
Click image for larger version

Name:	cts192-solar.png
Views:	318
Size:	29.6 KB
ID:	4050  
__________________

WannaBeFree is offline   Reply With Quote
Old 04-28-2017, 03:30 PM   #2
Senior Member
 
ewarnerusa's Avatar
 
Join Date: Dec 2011
Location: Helena, MT
Posts: 606
Montana
Are they 12V nominal panels? What about putting the pairs of 100 W in series and have three parallel arrays? Is this what Renogy says won't work because I can't see why? Put a combiner box on the roof and run 4 gauge from the combiner to your controller.

I just bit the bullet and drilled a 1" diameter hole in my roof beneath the combiner box to get the wires inside. I was advised against trying to open up the walls to hide wires so I drilled my hole right at an interior corner and went with wire conduit along that wall corner and along the floor to get the wires to front of the TT to the pass through storage area where I mounted the controller. Then from the controller I went through the floor and along the underside of the frame to the batteries on the tongue which was about 5' of wire length. The underbelly of the TT is covered in coroplast so the wiring is not exposed on the underside.
__________________

__________________
2012 Aspen Trail 2710BH | 470 watts of solar on the roof | 2x6V GC batteries | 1500 watt PSW inverter | Micro Air on A/C | so far strictly boondocking
ewarnerusa is offline   Reply With Quote
Old 04-30-2017, 02:07 AM   #3
Senior Member
 
Join Date: Nov 2016
Location: Alexandria
Posts: 101
Virginia
Hi ewarnerusa,

Yes they are 12V nominal panels - https://www.renogy.com/renogy-100-wa...e-solar-panel/. Just checked and these are pricier now. A while back Amazon had them for about $100 so I might look at other alternative panels.

Renogy said I could connect the panels in series to get around some of the problem (I could use a lighter gauge wire if in series vs parallel) but I really want to run them all in parallel to prevent power loss when only a single panel is shaded.

I'm not familiar with combiner boxes and did a search - https://www.altestore.com/store/encl...in-rail-p10397. Is the type of combiner box you placed on your roof?

Running the wiring through conduit in the trailer sounds like a much better idea instead of through the wall or worse yet along the front of the coach. I was looking around at conduit and found this for running under the trailer - https://www.walmart.com/ip/AFC-Cable...nduit/47502185. This looks like it could take some abuse

Thanks!
WannaBeFree is offline   Reply With Quote
Old 04-30-2017, 06:59 PM   #4
Senior Member
 
sundancer 87's Avatar
 
Join Date: Dec 2012
Location: Tahlequah
Posts: 3,079
Oklahoma
Quote:
Originally Posted by WannaBeFree View Post
Hi ewarnerusa,

Yes they are 12V nominal panels - https://www.renogy.com/renogy-100-wa...e-solar-panel/. Just checked and these are pricier now. A while back Amazon had them for about $100 so I might look at other alternative panels.

Renogy said I could connect the panels in series to get around some of the problem (I could use a lighter gauge wire if in series vs parallel) but I really want to run them all in parallel to prevent power loss when only a single panel is shaded.

I'm not familiar with combiner boxes and did a search - https://www.altestore.com/store/encl...in-rail-p10397. Is the type of combiner box you placed on your roof?

Running the wiring through conduit in the trailer sounds like a much better idea instead of through the wall or worse yet along the front of the coach. I was looking around at conduit and found this for running under the trailer - https://www.walmart.com/ip/AFC-Cable...nduit/47502185. This looks like it could take some abuse

Thanks!
Take a look at the Carlon electrical products page. The green field will work but the Carlon PVC conduit is much easier to work.
Carlon Sales | Purchase Carlon Conduit, Floor Boxes, Enclosures, Wireway, & More!
__________________
2013 Voltage 3800, 2012 Chevy 3500 HD
2010 Yamaha V Star 950
2009 Yamaha Raider
Volunteering with Habitat for Humanity Caravanners
sundancer 87 is offline   Reply With Quote
Old 04-30-2017, 07:08 PM   #5
Senior Member
 
ewarnerusa's Avatar
 
Join Date: Dec 2011
Location: Helena, MT
Posts: 606
Montana
By combiner box I meant any type of wire distribution method enclosed in a weather protected case. What you posted will work. I used a distribution block like at the following link that I put inside a wire conduit box that I bought from the hardware store.
XScorpion 4 / 8 Gauge Distribution Block - Darvex.com
__________________
2012 Aspen Trail 2710BH | 470 watts of solar on the roof | 2x6V GC batteries | 1500 watt PSW inverter | Micro Air on A/C | so far strictly boondocking
ewarnerusa is offline   Reply With Quote
Old 05-01-2017, 03:59 AM   #6
Senior Member
 
Join Date: Nov 2016
Location: Alexandria
Posts: 101
Virginia
Thanks sundancer 87,

I'll check out the PVC conduit. Should it be about as rugged when running under a trailer? One big positive with the PVC is no rust as compared to the steel conduit
WannaBeFree is offline   Reply With Quote
Old 05-01-2017, 04:53 AM   #7
Senior Member
 
Join Date: Nov 2016
Location: Alexandria
Posts: 101
Virginia
Thanks ewarnerusa,

Looking at the distribution block page I see - "One 4 gauge input with four 8 gauge outputs". Not really for sure what this does. I'm guessing you plug up to four solar panel positive leads into the 8-gauge side and one 4 gauge positive lead comes out the other side. I'm not for sure what this would do to the volts and amps but I'm guessing it would be like a parallel connection as you are essentially connecting positive to positive for each of the 8 gauge inputs. And then for the negative wires from the panels I'm guessing you would use another distribution block?

Also, are you aware of a web site which shows the voltage drop over 4 and 8 gauge wires based upon wire length? If I can run the 8 gauge wires from the panels as far as ~ 20' (from the rear of the TT to the front) and then feed the panel wires into the distribution block, I would then need about 12' of 4 gauge wire to drop from the roof, through the floor, and out to the battery box with the charge controller.

Combining two panels in series would give me about 24V. I'm sure I would lose some voltage over the ~ 20' run from the rear of the TT to the front and ~ 12’ from the roof top to the battery compartment but with a 50% loss in voltage I'd still be at 12V. I'd be losing power in both panels when only one panel of a pair is shaded but it sounds like this would work.
WannaBeFree is offline   Reply With Quote
Old 05-01-2017, 12:53 PM   #8
Senior Member
 
sundancer 87's Avatar
 
Join Date: Dec 2012
Location: Tahlequah
Posts: 3,079
Oklahoma
Quote:
Originally Posted by WannaBeFree View Post
Thanks sundancer 87,

I'll check out the PVC conduit. Should it be about as rugged when running under a trailer? One big positive with the PVC is no rust as compared to the steel conduit
Just as rugged and lighter and easier to cut. The blue flexible conduit can be cut with a sharp knife and is great to work also. My local electrical supply house doesn't sell it anymore but maybe that's just them.
__________________
2013 Voltage 3800, 2012 Chevy 3500 HD
2010 Yamaha V Star 950
2009 Yamaha Raider
Volunteering with Habitat for Humanity Caravanners
sundancer 87 is offline   Reply With Quote
Old 05-01-2017, 03:10 PM   #9
Senior Member
 
ewarnerusa's Avatar
 
Join Date: Dec 2011
Location: Helena, MT
Posts: 606
Montana
Quote:
Originally Posted by WannaBeFree View Post
Thanks ewarnerusa,

Looking at the distribution block page I see - "One 4 gauge input with four 8 gauge outputs". Not really for sure what this does. I'm guessing you plug up to four solar panel positive leads into the 8-gauge side and one 4 gauge positive lead comes out the other side. I'm not for sure what this would do to the volts and amps but I'm guessing it would be like a parallel connection as you are essentially connecting positive to positive for each of the 8 gauge inputs. And then for the negative wires from the panels I'm guessing you would use another distribution block?
Yes, you got it. It doesn't do anything to your volts and amps, that depends on how you tie the panels into your combiner bus. You have essentially provided an extension of the charge controller inputs to the TT roof, so tie them in however you see fit.

Quote:
Originally Posted by WannaBeFree View Post
Also, are you aware of a web site which shows the voltage drop over 4 and 8 gauge wires based upon wire length? If I can run the 8 gauge wires from the panels as far as ~ 20' (from the rear of the TT to the front) and then feed the panel wires into the distribution block, I would then need about 12' of 4 gauge wire to drop from the roof, through the floor, and out to the battery box with the charge controller.
Here's what google found for me.
Voltage Drop Calculator
Your 8 gauge to the combiner box and 4 gauge from there to the controller is exactly what I was describing. I would feel good about that setup on my camper.

Quote:
Originally Posted by WannaBeFree View Post
Combining two panels in series would give me about 24V. I'm sure I would lose some voltage over the ~ 20' run from the rear of the TT to the front and ~ 12’ from the roof top to the battery compartment but with a 50% loss in voltage I'd still be at 12V. I'd be losing power in both panels when only one panel of a pair is shaded but it sounds like this would work.
I personally wouldn't worry about it, you've got the potential to exceed C/10 charge rate anyway so think of it as built in protection for your batteries from too high of a charge current. :-)
__________________
2012 Aspen Trail 2710BH | 470 watts of solar on the roof | 2x6V GC batteries | 1500 watt PSW inverter | Micro Air on A/C | so far strictly boondocking
ewarnerusa is offline   Reply With Quote
Old 05-01-2017, 06:24 PM   #10
Senior Member
 
Join Date: Nov 2016
Location: Alexandria
Posts: 101
Virginia
Thanks sundancer 87,

That blue flexible conduit sounds like the way to go
WannaBeFree is offline   Reply With Quote
Old 05-01-2017, 06:42 PM   #11
Senior Member
 
Join Date: Nov 2016
Location: Alexandria
Posts: 101
Virginia
Thanks ewarnerusa,

I really like that voltage drop calculator. I plugged in:

Phase - Single
Conductor - Copper
Installation - Overhead
Voltage - 24
Maximum voltage drop - 50
Length of cable run - 20
Current at the end of cable run 30

And it returned #10 Copper conductor will limit the voltage drop to 5.25% or less at 30A for 20' and 24V. It appears that 8 gauge should work out very nicely :-)

And C/10 charge rate. I had never heard of that. When I searched for details C/10 is the "ideal peak charge" for your battery bank. In my case 207x2 = 414 = C and C/10 = 414/10 = 41.4. According to the Renogy guys I can expect ~ 5A from each panel so with surges I could be exceeding C/10. So like you say the shading could be a good thing for the batteries.

Thanks!
WannaBeFree is offline   Reply With Quote
Old 05-01-2017, 06:51 PM   #12
Senior Member
 
ewarnerusa's Avatar
 
Join Date: Dec 2011
Location: Helena, MT
Posts: 606
Montana
Yeah, I wouldn't lose any sleep over exceeding C/10. It would take a lot of just-right conditions to get there. Seems like you'll have a pretty nice solar setup. Whatchya running with all that capacity? Is there an inverter in there as well?
__________________
2012 Aspen Trail 2710BH | 470 watts of solar on the roof | 2x6V GC batteries | 1500 watt PSW inverter | Micro Air on A/C | so far strictly boondocking
ewarnerusa is offline   Reply With Quote
Old 05-01-2017, 07:52 PM   #13
Senior Member
 
Join Date: Nov 2016
Location: Alexandria
Posts: 101
Virginia
My wife and I both use CPAPS.

Stats for one is:
DC Power Consumption: 12 VDC, 5.0 A

Stats for the other is:
DC 24V 1.25A (FG) and 3.75 (Sys)

I'm pretty sure the first includes power consumption for the heated water chamber so maybe the unit will use less than half that amount.

For the second one I think the (FG) number corresponds to not using the heated chamber and hose. I think the 12V load would be 2.5A using W=24V*1.25A=30W and A=W/V=30W/12V=2.5A at 12V.
So maybe we're consuming 2.5A (assuming the first only consumes 1/2 of max without heated chamber)+2.5A (second cpap)=5A, 5A * 8H = 40AH. The second CPAP uses some sort of transformer to go from 12V to 24V so I'm sure there is some inefficiency there so maybe these numbers are closer to 50AH for 8 hours.

On top of that notebooks, tablets, cell phones, Cell Booster, device battery charging, LED lighting, Fan-Tastic Fan, Endless Breeze Fan, Chromecast, 32" to 40" LED TV (going for an annual energy cost around $5-$6). I want to use 12V where ever possible but I have not found 12V adapters for the notebooks and DSLR batteries. For the TV I'm buying one which has a notebook style power brick which provides 12V instead of AC. Supposedly you can get a cable from Radio Shack with multiple tips which allows the TV to be plugged into a 12V socket. For the notebooks and DSLR battery charging I’m thinking I’ll get a 300W pure sine inverter. I think with restricted use on these devices I should be able to keep the depth of discharge under 50% for the 414AH bank.

I’m also considering a modified sine wave inverter for powering devices like coffee bean grinders if I find I consistently have excess power.

I’m thinking I might need to start each day with bulk charging the batteries to ~ 90% using a Champion 2000W generator and then let the solar top off the bank. Also, I’m a bit concerned the 414AH bank will not be sufficient so I may add a couple more batteries. Pretty cheap upgrade with Costco only charging $85+$15 core fee per battery.

Do you have any thoughts on alternatives to Renogy 100W mono panels and the Renogy 40 Amp Commander MPPT?

Thanks!
WannaBeFree is offline   Reply With Quote
Old 05-01-2017, 08:58 PM   #14
Senior Member
 
ewarnerusa's Avatar
 
Join Date: Dec 2011
Location: Helena, MT
Posts: 606
Montana
I only have experience with the stuff I installed: Cynergy 140 watt 12V panels and a Morningstar Tristar 45 PWM. The controller is really nice, fully user programmable via a PC interface in addition to several default charging profiles, and offers diversion load support. That might be something you may be interested if you do indeed find you have excess solar capacity. Diversion load will allow you convert any excess solar current to another load such as a water heater element. I'm not sure how unique that feature is, but it is pretty cool. They offer an MPPT version of the Tristar but it is expensive at nearly $500 for the 45 amp one.

I don't think there is anything unique or special about my Cynergy panels. They were simply well-priced when I bought them from solarblvd.com so I bought 2. They keep coming down in price so I'm always tempted to buy more and fill up my controller capacity, but I haven't had a need for more solar so I never have.
__________________
2012 Aspen Trail 2710BH | 470 watts of solar on the roof | 2x6V GC batteries | 1500 watt PSW inverter | Micro Air on A/C | so far strictly boondocking
ewarnerusa is offline   Reply With Quote
Old 05-03-2017, 05:20 AM   #15
Senior Member
 
Join Date: Nov 2016
Location: Alexandria
Posts: 101
Virginia
Thanks ewarnerusa,

I'll have to check out these panels and controller :-)
__________________

WannaBeFree is offline   Reply With Quote
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


» Featured Campgrounds

Reviews provided by

Disclaimer:

This website is not affiliated with or endorsed by Dutchmen RV or any of its affiliates. This is an independent, unofficial site.


All times are GMT. The time now is 12:07 PM.


Powered by vBulletin® Version 3.8.7
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Copyright 2020 Social Knowledge, LLC All Rights Reserved.
×