06-12-2016, 09:30 AM
|
#1
|
Senior Member
Join Date: Aug 2013
Location: Memphis
Posts: 1,616
Michigan
|
Power problems yet again
Headed to MIS Thursday for the races. Came home Friday evening - generator kept overheating and shutting off - was getting so hot the hot metal smell scared us a bit. Called a few places and no one on standby for mobile service to include Onan. Way too hot to try to tough it out. Wife is very soured on camping period now especially in the Voltage.
Brought it home and did lots of reading yesterday. Turns out it appeared to be my choice of running a synthetic oil in it when I changed oil and filter at 40 hours. I changed the oil and filter yesterday putting SAE 30 in it and it ran for over 6 hours yesterday under load without a hiccup.
Only thing I am still fighting now is the Load Management System still occasionally sheds all the loads and then resets itself. We had that last year at the fall race. More an annoyance than anything as you then have reset all the clocks and retune the DirecTV.
Looking for any help on the LMS - called the company last year after I received info from Cale and they were no help.
But people - run SAE 30 in your generators - friend that owns a small engine shop tells me SAE 30 for ANY air cooled engine. The synthetics and other lighter weight oils do not have the cooling properties. I am a believer.
__________________
__________________
2019 Ram 3500 Limited w/ Max Tow pkg
2005 Cardinal 33LX
2014-3950, Full Paint, 17.5" tires, 370W solar, 3100W Magnum inverter w/ AGS, 7500w diesel generator, Micro-Air Easy Start 364 (x3) SOLD!
|
|
|
06-12-2016, 10:04 AM
|
#2
|
Senior Member
Join Date: Sep 2014
Location: Callaway
Posts: 864
Maryland
|
I completely agree on the SAE 30. I switched oils prior to my cross country trip last year and had zero problems from the genset. I am using Royal Purple...I may pull a sample and send in for testing on the next change, I am half way through the oil change interval on this one.
Cale
__________________
__________________
TV: 2015 F-350 DRW, CC, 4x4, with 14k GVWR package, 98 gallon TransferFlow Aux Tank, Timbren Shocks
TH: 2014 Voltage 3950, Sailun S637 all around
|
|
|
06-12-2016, 01:44 PM
|
#3
|
Senior Member
Join Date: Feb 2014
Location: Tucson
Posts: 872
Arizona
|
I disagree that ALL air cooled engines use 30w oil. My air cooled Harley runs on 20w-50 full synthetic oil, which is THE recommended oil from the maker. In air cooled engines full synthetic oil is the way to go as it doesn't break down under the extreme heat like dino oil does and the engine runs cooler.
__________________
2014 Voltage 3600
2013 Chevy 3500 CC DRW
2019 RZR 1000XP Trails and Rocks Edition
|
|
|
06-12-2016, 02:11 PM
|
#4
|
Senior Member
Join Date: Aug 2013
Location: Memphis
Posts: 1,616
Michigan
|
Manufacture of these Onan gens recommend SAE30 for hotter conditions and the guy making the recommendation is a small engine guy not a Harley guy. After my experience the other day and yesterday, I'll only use SAE30 in my small air cooled engines. Also the Onan rep told me that the synthetics just don't have the cooling properties required by these small, enclosed engines. With the syn oil, we thought the gen was going to burn up it was so hot and smelled of hot metal. Governer started surging the engine to the extreme that it was shutting down.
Sent from my SM-G920V using Tapatalk
__________________
2019 Ram 3500 Limited w/ Max Tow pkg
2005 Cardinal 33LX
2014-3950, Full Paint, 17.5" tires, 370W solar, 3100W Magnum inverter w/ AGS, 7500w diesel generator, Micro-Air Easy Start 364 (x3) SOLD!
|
|
|
06-12-2016, 02:37 PM
|
#5
|
Site Team
Join Date: Jun 2014
Location: Sprung Leak
Posts: 3,157
North Carolina
|
Quote:
Originally Posted by azdryheat
I disagree that ALL air cooled engines use 30w oil. My air cooled Harley runs on 20w-50 full synthetic oil, which is THE recommended oil from the maker. In air cooled engines full synthetic oil is the way to go as it doesn't break down under the extreme heat like dino oil does and the engine runs cooler.
|
Harley is moving and has air going across at a better rate than a static enclosed generator. I use what the manufacturer recommends. In this case, 30 w it is. Synthetics may or may not provide the necessary heat transfer in smaller engines.
I have a water cooled Honda CH125, I was riding with a buddy of mine one weekend out in the Las Vegas area, he was on an air cooled Lambretta, he was losing power and struggling, the Honda just kept chugging along. Each system has it's advantages and disadvantages.
Aaron
__________________
There is madness to my methods
2015 Coleman CM16FBS(traded) 2016 Concord 300DS
2015 Ford Fusion Hybrid following along
|
|
|
06-12-2016, 04:57 PM
|
#6
|
Senior Member
Join Date: Jan 2015
Location: Roselle
Posts: 1,292
Illinois
|
Just my humble opinion, but I use what the manufacturer recommends. HD spends hundreds of millions of dollars on R and D. If they say use HD 20-50 synthetic, that's what I use. Same with my Onan generator; Onan oil. Not that much more expensive and you're not changing it all that often anyway.
Rusty
__________________
2015 Black F-350 Platinum Diesel Dually Crew Cab
2019 Riverstone Legacy 38MB (Full Paint/All Options)
2015 Voltage 3990 (Full Paint, All Options) Sold 6/18
2005 Harley Ultra Classic w/too many miles
|
|
|
06-13-2016, 02:11 PM
|
#7
|
Senior Member
Join Date: Aug 2013
Location: Memphis
Posts: 1,616
Michigan
|
Quote:
Originally Posted by lcv800
Just my humble opinion, but I use what the manufacturer recommends. HD spends hundreds of millions of dollars on R and D. If they say use HD 20-50 synthetic, that's what I use. Same with my Onan generator; Onan oil. Not that much more expensive and you're not changing it all that often anyway.
Rusty
|
I actually will be. 3-4 NASCAR races per year dry camping. One of which is 6 days in stupid-hot Darlington in August. Generator runs 24/7 there. Oil change interval is 150-hours if memory serves...but I am agreeing on the viscosity, just maybe not the brand in all cases
Sent from my SM-G920V using Tapatalk
__________________
2019 Ram 3500 Limited w/ Max Tow pkg
2005 Cardinal 33LX
2014-3950, Full Paint, 17.5" tires, 370W solar, 3100W Magnum inverter w/ AGS, 7500w diesel generator, Micro-Air Easy Start 364 (x3) SOLD!
|
|
|
06-17-2016, 04:31 PM
|
#8
|
Senior Member
Join Date: Aug 2013
Location: Memphis
Posts: 1,616
Michigan
|
May have isolated the issue to the bedroom AC unit. All was running great on the genny in the driveway - main AC, garage AC, electric water heater, TV, both refers, ice maker. Bed room AC compressor kicked and lost power. With only bedroom AC fan on, all is well. I am going to climb on the roof and check my capacitors. I installed a hard start awhile back, so will check all connections as well. Fingers crossed!
__________________
2019 Ram 3500 Limited w/ Max Tow pkg
2005 Cardinal 33LX
2014-3950, Full Paint, 17.5" tires, 370W solar, 3100W Magnum inverter w/ AGS, 7500w diesel generator, Micro-Air Easy Start 364 (x3) SOLD!
|
|
|
07-05-2016, 11:54 PM
|
#9
|
Senior Member
Join Date: Aug 2013
Location: Memphis
Posts: 1,616
Michigan
|
Narrowed further yet. Out camping this weekend on 30A service. Main and bedroom AC ran fine. LMS did show a spike of 57A when bedroom AC compressor kicked in but she held and ran. So....Only happens when running generator power...
Sent from my SM-G920V using Tapatalk
__________________
2019 Ram 3500 Limited w/ Max Tow pkg
2005 Cardinal 33LX
2014-3950, Full Paint, 17.5" tires, 370W solar, 3100W Magnum inverter w/ AGS, 7500w diesel generator, Micro-Air Easy Start 364 (x3) SOLD!
|
|
|
07-11-2016, 10:32 PM
|
#10
|
Senior Member
Join Date: Jan 2016
Location: Readfield
Posts: 137
Maine
|
Quote:
Originally Posted by donzinger
May have isolated the issue to the bedroom AC unit. All was running great on the genny in the driveway - main AC, garage AC, electric water heater, TV, both refers, ice maker. Bed room AC compressor kicked and lost power. With only bedroom AC fan on, all is well. I am going to climb on the roof and check my capacitors. I installed a hard start awhile back, so will check all connections as well. Fingers crossed!
|
Can you point me in the direction of what CAPs you purchased? How much of a job was it?
|
|
|
07-11-2016, 10:50 PM
|
#11
|
Senior Member
Join Date: Aug 2013
Location: Memphis
Posts: 1,616
Michigan
|
Supco SPP6. Amazon is one source. Very easy to install. Piggyback onto existing ones.
Sent from my SM-G920V using Tapatalk
__________________
2019 Ram 3500 Limited w/ Max Tow pkg
2005 Cardinal 33LX
2014-3950, Full Paint, 17.5" tires, 370W solar, 3100W Magnum inverter w/ AGS, 7500w diesel generator, Micro-Air Easy Start 364 (x3) SOLD!
|
|
|
07-11-2016, 11:33 PM
|
#12
|
Senior Member
Join Date: Aug 2013
Location: Memphis
Posts: 1,616
Michigan
|
Sent from my SM-G920V using Tapatalk
__________________
2019 Ram 3500 Limited w/ Max Tow pkg
2005 Cardinal 33LX
2014-3950, Full Paint, 17.5" tires, 370W solar, 3100W Magnum inverter w/ AGS, 7500w diesel generator, Micro-Air Easy Start 364 (x3) SOLD!
|
|
|
07-11-2016, 11:39 PM
|
#13
|
Senior Member
Join Date: Jan 2016
Location: Readfield
Posts: 137
Maine
|
Quote:
Originally Posted by donzinger
Sent from my SM-G920V using Tapatalk
|
Thanks! Looks like you have already gone through many of the upgrades, and lessons I will be going through...
Sent from my Nexus 6P using Tapatalk
|
|
|
07-11-2016, 11:40 PM
|
#14
|
Senior Member
Join Date: Aug 2013
Location: Memphis
Posts: 1,616
Michigan
|
Oh yeah. All over the mods page!
Sent from my SM-G920V using Tapatalk
__________________
2019 Ram 3500 Limited w/ Max Tow pkg
2005 Cardinal 33LX
2014-3950, Full Paint, 17.5" tires, 370W solar, 3100W Magnum inverter w/ AGS, 7500w diesel generator, Micro-Air Easy Start 364 (x3) SOLD!
|
|
|
07-28-2016, 02:50 PM
|
#15
|
Senior Member
Join Date: Oct 2014
Location: Smith
Posts: 489
Nevada
|
Curious about connection for spp6..what's the correct way to hook up. Just received my parts
Sent from my iPhone using Tap
2014 V3005 Voltage Toy Hauler
2012 Dodge Ram 2500. Firestone Bags. 1 ton+ leaf spring pack basically stock
__________________
Bill gran
2014 v3005 voltage
Dodge Ram 2500 bagged stock
|
|
|
07-28-2016, 02:54 PM
|
#16
|
Senior Member
Join Date: Aug 2013
Location: Memphis
Posts: 1,616
Michigan
|
If your existing capacitor has a connection labeled "HERM" connect one lead on it and the other to "-". The capacitor does not care about polarity. If your existing one does not have a "HERM" terminal, just use "+" & "-". You will leave the existing inn place and just piggyback me one onto it.
Sent from my SM-G920V using Tapatalk
__________________
2019 Ram 3500 Limited w/ Max Tow pkg
2005 Cardinal 33LX
2014-3950, Full Paint, 17.5" tires, 370W solar, 3100W Magnum inverter w/ AGS, 7500w diesel generator, Micro-Air Easy Start 364 (x3) SOLD!
|
|
|
07-28-2016, 03:06 PM
|
#17
|
Senior Member
Join Date: Oct 2014
Location: Smith
Posts: 489
Nevada
|
Curious about connection for spp6..what's the correct way to hook up. Just received my partsy
__________________
Bill gran
2014 v3005 voltage
Dodge Ram 2500 bagged stock
|
|
|
07-28-2016, 03:08 PM
|
#18
|
Senior Member
Join Date: Jan 2016
Location: Readfield
Posts: 137
Maine
|
Donz is correct, these are not polarity dependent
Sent from my Nexus 6P using Tapatalk
|
|
|
07-28-2016, 03:09 PM
|
#19
|
Senior Member
Join Date: Oct 2014
Location: Smith
Posts: 489
Nevada
|
Thank you!!!!!!
Sent from my iPhone using Tap
2014 V3005 Voltage Toy Hauler
2012 Dodge Ram 2500. Firestone Bags. 1 ton+ leaf spring pack basically stock
__________________
Bill gran
2014 v3005 voltage
Dodge Ram 2500 bagged stock
|
|
|
08-04-2016, 01:06 PM
|
#20
|
Senior Member
Join Date: Nov 2015
Location: Quarantine
Posts: 365
Ontario
|
Quote:
Originally Posted by wahoonc
Harley is moving and has air going across at a better rate than a static enclosed generator.
|
I suspect that in many circumstances, there is more air moving through our Onan than our Harleys.