I have a 2013 Voltage 3905. I was running the generator today and had power to all outlets. I started vacuuming and the power went out in the outlet I was using. Sounds like a breaker or GFI right? Turns out, all but 3 outlets in the unit are not working. The GFI and the two outlets on the island are working. None of the others work. The GFI, breakers and all fuses (that I could find) have been checked and seem to be fine. I went all through the unit thinking there might be another GFI somewhere with no luck. Any suggestions?
|
Hi
I had this same unit . There're a total of 8 GFI in my unit .
1 master bath
2 in kitchen island
1 washer/dryer hook up
2 by ramp door (inside the toy hauler )
1 outside the front door
1 inside the water hook up
This happened to us as well. What it was the GFI. In the master bath had a dim green light on . So I checked it with my meter and it showed 70volts . So I replaced it and problem solve. So if you have a meter check all the GFI to see witch one is not giving you 120volts after you reset it . Hope this helps.
John