Old 05-06-2015, 10:18 PM   #1
Senior Member
 
Join Date: Jan 2015
Location: Roselle
Posts: 1,292
Illinois
Generator Stalling

I know this was discussed a bit ago and the consensus was probably a fuel pump issue, but I'd like some opinions before I God forbid, go in for warranty work. New unit with a Onan 5500. Has 3 hours on it. Runs for a bit then dies out. Need to wait 5-10 minutes and starts right up. Seems to run a bit longer each time I start. Last time about 30 minutes or so. Should I keep running it in hopes of divine intervention and it gets better, or do I take it in. Have an appointment at CW in Wauconda Illinois to have my solar panels installed Friday. That they said I could wait for that and take it home. If they do warranty work on the generator, maybe a three week wait between diagnosis, warranty submittal, approval, parts order, then finally installation. Not a handy guy so anything beyond adjusting or cleaning could beyond my skill set. Thoughts? Thanks,
Rusty
__________________

__________________
2015 Black F-350 Platinum Diesel Dually Crew Cab
2019 Riverstone Legacy 38MB (Full Paint/All Options)
2015 Voltage 3990 (Full Paint, All Options) Sold 6/18
2005 Harley Ultra Classic w/too many miles
lcv800 is offline   Reply With Quote
Old 05-06-2015, 10:37 PM   #2
Senior Member
 
Join Date: Oct 2013
Location: South East
Posts: 234
Mississippi
Dump a can of sea foam in fuel tank. If tank is full add 2 cans. Let sea foam settle in fuel tank for a few hours, then start generator and let it run until it dies. May have to put a load on it. Next day start generator and after 15 minutes start putting load on genset and leave running for hours. I run mine every 2 weeks with load and I also use ethanol free gasoline.
__________________

__________________
David
2014 Voltage 3950
2013 F-350 DRW Lariat
lakebuster is offline   Reply With Quote
Old 05-06-2015, 10:37 PM   #3
Senior Member
 
Join Date: Mar 2014
Location: Desert Hot Springs
Posts: 1,761
California
Take the fuel cap off & see if that makes a difference. Could be its creating a vacuum.
__________________
Mike
2002 42' Monaco Signature Triple Crown tow 2014 F-150
2014 Voltage V3605 Sold 5/3/17
2012 F-350 6.7l CC 4X4, Sold 10/10/17
DesertRat is offline   Reply With Quote
Old 05-06-2015, 11:34 PM   #4
Senior Member
 
Join Date: Dec 2014
Location: Minden
Posts: 707
Nevada
Could be some old gas, left over from when they build it, Do what lakebuster stated, then make sure you run it a couple times a month, just to keep the old gas from messing up the Carburetor and fuel filter
__________________
Rich and Angela, Lab Dogs, Ruben, Ace
2015 Voltage V3895
2006 Lance Truck Camper 1181
2019 GMC 3500HD 4X4 CC DRW LB Bags Husky 26K Hitch Can Am Commander 1000 ATV
RVNevada is offline   Reply With Quote
Old 05-07-2015, 12:44 AM   #5
Senior Member
 
HornedToad's Avatar
 
Join Date: Mar 2014
Location: Midland
Posts: 606
Texas
X3 on the SeaFoam...

If you think it's the fuel pump try starting the generator from the control on the front of the unit. When you press the start button down to prime and you should be able hear the fuel pump cycle. Changing the fuel filter is easy, and the first thing to try if you think you had bad gas, you'll be able to find one that will fit off the shelf at an auto parts store.

My front pump tank was slow to fill due to a kink in one of the vent lines. I believe this would cause a vacuum issue as mentioned above if it was on the rear generator tank.

You may also want to review an extensive post from another forum about troubleshooting Onan generator issues, that were ultimately attributed to the EMS, but covers all the bases and includes several hands on videos...

Onan 5500 not starting...partially solved
__________________

Mike & Helen
2014 Voltage 3895 EPIC III
2013 Ford F350 CC DRW FX4
HornedToad is offline   Reply With Quote
Old 05-07-2015, 01:16 AM   #6
Senior Member
 
Join Date: Jan 2015
Location: Roselle
Posts: 1,292
Illinois
Thanks for the insight. Drove out to the yard and added the Sea Foam. I'll test it out tomorrow and listen for the fuel pump and maybe the filter. Appreciate all the tips.
Rusty
__________________
2015 Black F-350 Platinum Diesel Dually Crew Cab
2019 Riverstone Legacy 38MB (Full Paint/All Options)
2015 Voltage 3990 (Full Paint, All Options) Sold 6/18
2005 Harley Ultra Classic w/too many miles
lcv800 is offline   Reply With Quote
Old 05-07-2015, 02:20 AM   #7
Senior Member
 
HornedToad's Avatar
 
Join Date: Mar 2014
Location: Midland
Posts: 606
Texas
Rusty,


When you get your generator up and running Onan recommends the following break in procedure...


Breaking In Your New Generator






Your generator will perform better if you follow the break-in procedure


recommended in the Operator’s Manual. The break-in process typically involves


running the generator at about 50 percent load for two hours, then at about 75


percent load for two hours, then letting it cool down. You should change the engine


crankcase oil after the fi rst 20 hours of operation, and every 100 to 150 hours


thereafter.


__________________

Mike & Helen
2014 Voltage 3895 EPIC III
2013 Ford F350 CC DRW FX4
HornedToad is offline   Reply With Quote
Old 05-07-2015, 03:46 AM   #8
Senior Member
 
Join Date: Sep 2014
Location: Okeana
Posts: 183
Ohio
I am fighting this issue as well. Post what ever solution seems to work.
__________________
2014 F-250 6.7 with Timbrens
2015 Voltage 3605
jeffwelsh is offline   Reply With Quote
Old 05-07-2015, 04:24 AM   #9
Senior Member
 
HornedToad's Avatar
 
Join Date: Mar 2014
Location: Midland
Posts: 606
Texas
DW and I were talking about going down to the gulf coast this Memorial Day and it made me remember the altitude adjustment screw on the Onan Generator.

This probably is not the issue as it does not have to be spot on. Mine is set @ 3,000 ft were I live. The stomping grounds I roam without adjusting for the altitude vary from 500 to 3,500 ft and I've never noticed a difference.

Now if it's turned up to 10,000 ft and your @ 1,000 that may be a problem?
__________________

Mike & Helen
2014 Voltage 3895 EPIC III
2013 Ford F350 CC DRW FX4
HornedToad is offline   Reply With Quote
Old 05-07-2015, 03:34 PM   #10
Senior Member
 
Join Date: Jan 2015
Location: Roselle
Posts: 1,292
Illinois
Thanks once again for all the tips. Followed everyones' suggestion, (Sea Foam, venting, listening for fuel pump, etc.) Ran it today for two hours while I re-routed my DISH box and re-installing the shelf in the closet, even putting it on 25% load for an hour. Ran perfectly until I was just about to shut it down, when it stalled. Since it is getting better every time, I will continue to fire it up whenever I get the chance until it goes away or gets worse. Decided not to have some technician tear it apart for diagnosis. I trust you experienced campers on the forum a lot more. Thanks for all the help.
Rusty
__________________
2015 Black F-350 Platinum Diesel Dually Crew Cab
2019 Riverstone Legacy 38MB (Full Paint/All Options)
2015 Voltage 3990 (Full Paint, All Options) Sold 6/18
2005 Harley Ultra Classic w/too many miles
lcv800 is offline   Reply With Quote
Old 05-07-2015, 03:51 PM   #11
Senior Member
 
Soccerloco's Avatar
 
Join Date: Oct 2014
Location: Smith
Posts: 489
Nevada
No problems on my cummins/onan 5500 wondering rather than going to rv dealer for warranty work if you could go direct to cummins. Here in northern Nevada we have Rocky Mountain Cummins. They service all cummins diesel plus do service on cummins/ onan generators. If so sure their work would be superior and much faster
__________________
Bill gran
2014 v3005 voltage
Dodge Ram 2500 bagged stock
Soccerloco is offline   Reply With Quote
Old 05-07-2015, 06:36 PM   #12
Senior Member
 
HornedToad's Avatar
 
Join Date: Mar 2014
Location: Midland
Posts: 606
Texas
A few more tips I always follow with my Onan...

I always start/stop the generator with no load. If you fire it up with any of the 120V AC items turned on it could cause the transfer switch to arc as it flips under load from the default shore power over to generator power. This would cause the contacts on the transfer switch to pit over time perhaps leading to a failure. Also, I always power down all of the 120V AC draw, especially the air conditioners, and let the generator idle for a minute or two before shut down. I never go to the trouble of flipping the breaker on the converter as it's a light load.

I mentioned earlier about finding a fuel filter at the auto parts store. You can also find an oil filters that fit, but I never use these as they are too short and difficult to remove. You can only get an air filter online or from Cummins. As was mentioned above I have a Cummins dealer nearby and I'll stop in and buy 4 quarts of oil, 2 of the Onan oil filters that are longer and stick out the bottom making them easier to remove and 1 air filter. I keep these on the trailer and religiously change the oil & filter every 100 to 150 hours and change the air filter every other time.

My last toy hauler was pre wired for a generator and I bought a 5500 Onan off eBay and installed it myself, with a little help from my friends. I put 500 hours on that generator with no problems. I got my Voltage last year and it has 400 hours on the Onan, also without a problem.

The Onans are very reliable units but the maintenance & service is important.
__________________

Mike & Helen
2014 Voltage 3895 EPIC III
2013 Ford F350 CC DRW FX4
HornedToad is offline   Reply With Quote
Old 05-08-2015, 12:14 PM   #13
Senior Member
 
Join Date: Jan 2015
Location: Roselle
Posts: 1,292
Illinois
Thank you. I'll follow your advice. Makes sense. Hopefully I'll be as fortunate with my unit.
Rusty
__________________
2015 Black F-350 Platinum Diesel Dually Crew Cab
2019 Riverstone Legacy 38MB (Full Paint/All Options)
2015 Voltage 3990 (Full Paint, All Options) Sold 6/18
2005 Harley Ultra Classic w/too many miles
lcv800 is offline   Reply With Quote
Old 05-21-2015, 12:26 AM   #14
Member
 
Join Date: May 2015
Location: elkton
Posts: 40
Maryland
check oil level just a little light will stall engine.
bill_covert is offline   Reply With Quote
Old 05-27-2015, 01:28 PM   #15
New Member
 
Join Date: May 2015
Location: MARIETTA
Posts: 8
Georgia
I just bought a Rubicon 2500 e/w a Onan 4000.
Has less than 5 hours on it. Initially it ran for 4 hours, then died. Now it runs for about 10 minutes, tries to stall a couple times and finally stalls. I have to reprime it for about a minute and the same cycle starts again. Brought it back to the dealer (RV World of Ga). They say it needs a new carb. ?

What I don't understand is 1) why they use a draped neoprene flexible fuel line that runs for 20+ feet in hangers every 2-3 feet. AND 2) at every hanger I have a pinched line due to the weight AND 3) the fuel pump is producing a vacuum to pull the fuel thru this restricted line. Why didn't they use a SS fuel line IF there wasn't a prime pump at the fuel tank? This is really a bad design. I can squeeze the line in my finger tips easily. WTF?
jwschull is offline   Reply With Quote
Old 05-27-2015, 01:32 PM   #16
New Member
 
Join Date: May 2015
Location: MARIETTA
Posts: 8
Georgia
And BTW, a SS fuel line is about 25.00/25 feet AND it will NEVER choke off the fuel due to a vacuum.
jwschull is offline   Reply With Quote
Old 05-27-2015, 03:14 PM   #17
Site Team
 
wahoonc's Avatar
 
Join Date: Jun 2014
Location: Sprung Leak
Posts: 3,157
North Carolina
Quote:
Originally Posted by jwschull View Post
I just bought a Rubicon 2500 e/w a Onan 4000.
Has less than 5 hours on it. Initially it ran for 4 hours, then died. Now it runs for about 10 minutes, tries to stall a couple times and finally stalls. I have to reprime it for about a minute and the same cycle starts again. Brought it back to the dealer (RV World of Ga). They say it needs a new carb. ?

What I don't understand is 1) why they use a draped neoprene flexible fuel line that runs for 20+ feet in hangers every 2-3 feet. AND 2) at every hanger I have a pinched line due to the weight AND 3) the fuel pump is producing a vacuum to pull the fuel thru this restricted line. Why didn't they use a SS fuel line IF there wasn't a prime pump at the fuel tank? This is really a bad design. I can squeeze the line in my finger tips easily. WTF?
Cause they cheap! the junk they used probably cost $3 vs the $22.50 for the good stuff times a few thousand units... equals profit in their pockets let the consumer deal with it.

Aaron
__________________

__________________
There is madness to my methods
2015 Coleman CM16FBS(traded) 2016 Concord 300DS
2015 Ford Fusion Hybrid following along
wahoonc is offline   Reply With Quote
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


» Featured Campgrounds

Reviews provided by

Disclaimer:

This website is not affiliated with or endorsed by Dutchmen RV or any of its affiliates. This is an independent, unofficial site.


All times are GMT. The time now is 08:42 AM.


Powered by vBulletin® Version 3.8.7
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Copyright 2020 Social Knowledge, LLC All Rights Reserved.
×