Old 10-31-2015, 11:15 AM   #1
Senior Member
 
Join Date: Sep 2014
Location: Callaway
Posts: 864
Maryland
Furnace Inop

Furnace has started acting up the last couple of days, now it seems to be completely Inop.

It has done a fairly decent job keeping the main living area with the given setting. Woke up yesterday to find that it was 5 degrees below the set point. I raised it 5 degrees to give it a 10 degree split and it kicked on. Now, I can set it to max temperature, the furnace will not kick on at all. I am going to file with Keystone online this morning, as my warranty ends tomorrow (1 Novemeber...impeccable timing).

Any thoughts as to what the problem may be?

Cale
__________________

__________________
TV: 2015 F-350 DRW, CC, 4x4, with 14k GVWR package, 98 gallon TransferFlow Aux Tank, Timbren Shocks

TH: 2014 Voltage 3950, Sailun S637 all around
calewjohnson is offline   Reply With Quote
Old 10-31-2015, 12:18 PM   #2
Site Team
 
wahoonc's Avatar
 
Join Date: Jun 2014
Location: Sprung Leak
Posts: 3,157
North Carolina
My first thought would be possibly a control board or the thermostat is going bad. I am not sure what type of furnace is in the unit you have or the controls system for it. I have one of the real simple ones that has a mechanical thermostat and a couple of limit switches.

Aaron
__________________

__________________
There is madness to my methods
2015 Coleman CM16FBS(traded) 2016 Concord 300DS
2015 Ford Fusion Hybrid following along
wahoonc is offline   Reply With Quote
Old 10-31-2015, 12:31 PM   #3
Senior Member
 
Join Date: Sep 2014
Location: Callaway
Posts: 864
Maryland
Quote:
Originally Posted by wahoonc View Post
My first thought would be possibly a control board or the thermostat is going bad. I am not sure what type of furnace is in the unit you have or the controls system for it. I have one of the real simple ones that has a mechanical thermostat and a couple of limit switches.

Aaron
Funny, as I sat here and read your reply, the furnace kicked on..did as it was suppose to. When the burner flipped off (while the fan was still running) I punched the temperature up a few degrees, the furnace lit off again...weird....

Have to wait for the wife to get out of bed, as the manuals are stored under there...

Cale
__________________
TV: 2015 F-350 DRW, CC, 4x4, with 14k GVWR package, 98 gallon TransferFlow Aux Tank, Timbren Shocks

TH: 2014 Voltage 3950, Sailun S637 all around
calewjohnson is offline   Reply With Quote
Old 10-31-2015, 01:10 PM   #4
Senior Member
 
Soccerloco's Avatar
 
Join Date: Oct 2014
Location: Smith
Posts: 489
Nevada
Had a similar issue on my last rv. Replaced digital thermostat everything was back to normal. Local rv dealer had thermostat $80 bought it on amazon for $30 same exact one.
__________________
Bill gran
2014 v3005 voltage
Dodge Ram 2500 bagged stock
Soccerloco is offline   Reply With Quote
Old 10-31-2015, 08:46 PM   #5
Senior Member
 
Join Date: Sep 2014
Location: Callaway
Posts: 864
Maryland
Think I fixed the problem...pulled the outside furnace cover off and found the controller board. Atwood was nice enough to have a sticker on the fan shroud that stated what failure codes were. Mine was one flash with three seconds off, restricted airflow...I thumped the fan shroud and she fired right up. Turned it all off and disassembled the fan...found a screw in the fan. Used some of the CRC slide lube and hit the top and bottom of the fan axle...put her all back together, tightened up screws and she works like a charm now. My only fear though is that the fan has apparently been restricted for some time now...may have shortened the life of the fan motor, as I would have assumed that it would spin freely, something like a frictionless bearing.

We will see.

Cale
__________________
TV: 2015 F-350 DRW, CC, 4x4, with 14k GVWR package, 98 gallon TransferFlow Aux Tank, Timbren Shocks

TH: 2014 Voltage 3950, Sailun S637 all around
calewjohnson is offline   Reply With Quote
Old 10-31-2015, 08:48 PM   #6
Senior Member
 
Soccerloco's Avatar
 
Join Date: Oct 2014
Location: Smith
Posts: 489
Nevada
Way to go!!! Love when things are solved by persistence! Cheers
__________________
Bill gran
2014 v3005 voltage
Dodge Ram 2500 bagged stock
Soccerloco is offline   Reply With Quote
Old 11-03-2015, 03:29 PM   #7
Senior Member
 
joebedford's Avatar
 
Join Date: Nov 2015
Location: Quarantine
Posts: 365
Ontario
I had a problem with my furnace. Turned out to be loose electrical connection. I thought I had it fixed several times because it would work for a while after wiggling / thumping. Eventually crimped all the push on connectors tighter and, fingers crossed, no problems since last year.
joebedford is offline   Reply With Quote
Old 11-03-2015, 09:22 PM   #8
Senior Member
 
Join Date: Feb 2015
Location: Plainfield
Posts: 120
Illinois
Our furnace wouldn't turn on at... Turns out the idiots at Dutchman do not check if the on/off -reset switch behind the outside furnace cover is turned on...
__________________
2009 F350 SRW 6.4 Diesel w/Spartan tuner, AFE exhaust, AFE cold air intake, Airlift 5000 ultimate bags with wireless air compressor.
2015 Voltage 3800 Epic 4 package
Pushin4u is offline   Reply With Quote
Old 11-04-2015, 02:56 AM   #9
Senior Member
 
Join Date: Jul 2014
Location: Dalzell
Posts: 714
South Carolina
Quote:
Originally Posted by Pushin4u View Post
Our furnace wouldn't turn on at... Turns out the idiots at Dutchman do not check if the on/off -reset switch behind the outside furnace cover is turned on...
You didn't check the furnace on your PDI when you bought it?????
MartyG is offline   Reply With Quote
Old 11-04-2015, 09:46 AM   #10
Senior Member
 
Join Date: Sep 2014
Location: Callaway
Posts: 864
Maryland
After pulling mine apart this weekend, I would suggest that everyone take the white cover apart and clean the trash out of that area. There was a red gas fitting end cap laying back there amongst some other trash.

Cale
__________________
TV: 2015 F-350 DRW, CC, 4x4, with 14k GVWR package, 98 gallon TransferFlow Aux Tank, Timbren Shocks

TH: 2014 Voltage 3950, Sailun S637 all around
calewjohnson is offline   Reply With Quote
Old 11-06-2015, 02:33 PM   #11
Senior Member
 
ATCguy's Avatar
 
Join Date: May 2013
Location: Cody
Posts: 1,764
Wyoming
Had a similar issue with mine this morning. (Yes, we had a cool snap out here the past 2 days)

Pulled the panel... One flash at 3 second intervals. Tapped the shroud a few times... no joy.

Came back inside... Turned thermostat off, then pulled the fuse for the furnace. Waited 30 seconds, replaced fuse, thermostat on, selected FURN. She started right up and is now operating as advertised.

Not sure what caused that. It worked fine yesterday morning. We did shut down all power & gas when the water heater was replaced yesterday, but can't imagine that would have done it.

Oh well...
__________________
Tom
2013 VOLTAGE 3200 (EPIC I & II)
2014 Ford F-450 PLATINUM
2018 BMW R1200GS RALLYE
ATCguy is offline   Reply With Quote
Old 11-06-2015, 03:54 PM   #12
Senior Member
 
Join Date: Sep 2014
Location: Callaway
Posts: 864
Maryland
Quote:
Originally Posted by ATCguy View Post
Had a similar issue with mine this morning. (Yes, we had a cool snap out here the past 2 days)

Pulled the panel... One flash at 3 second intervals. Tapped the shroud a few times... no joy.

Came back inside... Turned thermostat off, then pulled the fuse for the furnace. Waited 30 seconds, replaced fuse, thermostat on, selected FURN. She started right up and is now operating as advertised.

Not sure what caused that. It worked fine yesterday morning. We did shut down all power & gas when the water heater was replaced yesterday, but can't imagine that would have done it.

Oh well...
I would go ahead and shoot some lubricant on the shaft of the hamster wheel (top and bottom). After pulling mine apart, cleaning it all out, and lubricating it, she seems to run much quieter now.

Cale
__________________
TV: 2015 F-350 DRW, CC, 4x4, with 14k GVWR package, 98 gallon TransferFlow Aux Tank, Timbren Shocks

TH: 2014 Voltage 3950, Sailun S637 all around
calewjohnson is offline   Reply With Quote
Old 11-06-2015, 03:54 PM   #13
Senior Member
 
Join Date: Mar 2014
Location: Desert Hot Springs
Posts: 1,761
California
Quote:
Originally Posted by MartyG View Post
You didn't check the furnace on your PDI when you bought it?????
No I didn't check mine on the PDI. Did go on shake down trip directly from the dealer. It worked fine all weekend & ever sense
__________________
Mike
2002 42' Monaco Signature Triple Crown tow 2014 F-150
2014 Voltage V3605 Sold 5/3/17
2012 F-350 6.7l CC 4X4, Sold 10/10/17
DesertRat is offline   Reply With Quote
Old 11-06-2015, 05:44 PM   #14
Senior Member
 
joebedford's Avatar
 
Join Date: Nov 2015
Location: Quarantine
Posts: 365
Ontario
My furnace kept fooling me because it would work for a while, then it wouldn't come on. Cycling the power on the thermostat once or twice, then 3 - 4 times, then ten times would make it come on after which it would work for a while.

As I said earlier in this thread, the problems didn't really go away until I tightened the 'teeth' on the electrical spade lug connectors.
__________________

joebedford is offline   Reply With Quote
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


» Featured Campgrounds

Reviews provided by

Disclaimer:

This website is not affiliated with or endorsed by Dutchmen RV or any of its affiliates. This is an independent, unofficial site.


All times are GMT. The time now is 10:35 AM.


Powered by vBulletin® Version 3.8.7
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Copyright 2020 Social Knowledge, LLC All Rights Reserved.
×